Some Issues with JKBMS #333

Closed Answered by Louisvdw
fast-quality asked this question in Q&A
Discussion options

You must be logged in to vote

Hi Martin

When you make changes in utils.py, then yes you do need to reboot or else the changes will not apply.

The low voltage alarm at 48V will be coming from your BMS. When you set up your BMS the low voltage value for your battery should be less than the values in utils.py, so if you use the default 2.9V for the min cell voltage and you have a 15 cell battery then your BMS low voltage alarm should be less than that (2.9V x 15 = 43.5V). If not then the BMS will raise the low voltage alarm and the driver will publish that to the victron system.

The custom name that is not remembered is a known issue and will be changed in a future release.

Regards Louis